I am relatively new to coding in C, and I am trying to add a custom controller to the crazyflie firmware. I wanted to do some troubleshooting to make sure that the controller was receiving the correct state, and so I decided to log the state information in stabilizer.c after it was passed to the controller. From what I understand, the address of the state information is passed to the controller function in the main stabilizer loop here:

Code: Select all

 controller(&control, &setpoint, &sensorData, &state, tick);

Then, the controllers use the information as necessary. However, when logging the output of the state information directly from the controller script, the values seem to change drastically. I tried logging some state information from controller_pid.c and controller_mellinger.c to see if I made a mistake, but they were outputting the same conflated values. The controllers are all working fine, so I assume that I am somehow accessing the variables incorrectly when logging. I should note that the same state values are all outputted properly in the stateEstimate log block in stabilizer.c.

This picture shows the output of q1 (quanterion) from the the stateEstimate log group as I rotate the crazyflie, and it looks as expected:
Screen Shot 2020-06-30 at 9.19.47 PM.png
This picture shows the output of q1 from the log group in controller_pid.c as a I rotate the crazyflie.
Screen Shot 2020-06-30 at 9.33.13 PM.png
If you notice the y axis, the values have become huge, on the order of 10^9. Also, its hard to see in the picture, but if you look really closely, you can see that the value is changing as I rotate the crazyflie. It also jumps around +/- 10^9. This all leads me to believe that I am accessing the correct variable, but I am somehow scaling/changing it from what is originally in the state variable.

The following is my attempt at logging the state variables in controller_pid.c

Code: Select all

#include "stabilizer.h"
#include "stabilizer_types.h"

#include "attitude_controller.h"
#include "sensfusion6.h"
#include "position_controller.h"
#include "controller_pid.h"

#include "log.h"
#include "param.h"
#include "math3d.h"
#define ATTITUDE_UPDATE_DT    (float)(1.0f/ATTITUDE_RATE)

static bool tiltCompensationEnabled = false;
static bool pitchWithoutThrust = false;

static attitude_t attitudeDesired;
static attitude_t rateDesired;
static float actuatorThrust;

static float cmd_thrust;
static float cmd_roll;
static float cmd_pitch;
static float cmd_yaw;
static float r_roll;
static float r_pitch;
static float r_yaw;
static float accelz;

static float check;

static state_t statet;

void controllerPidInit(void)
{
  attitudeControllerInit(ATTITUDE_UPDATE_DT);
  positionControllerInit();
}

bool controllerPidTest(void)
{
  bool pass = true;

  pass &= attitudeControllerTest();

  return pass;
}

static float capAngle(float angle) {
  float result = angle;

  while (result > 180.0f) {
    result -= 360.0f;
  }

  while (result < -180.0f) {
    result += 360.0f;
  }

  return result;
}

void controllerPid(control_t *control, setpoint_t *setpoint,
                                         const sensorData_t *sensors,
                                         const state_t *state,
                                         const uint32_t tick)
{
  if (RATE_DO_EXECUTE(ATTITUDE_RATE, tick)) {
    // Rate-controled YAW is moving YAW angle setpoint
    if (setpoint->mode.yaw == modeVelocity) {
       attitudeDesired.yaw += setpoint->attitudeRate.yaw * ATTITUDE_UPDATE_DT;
    } else {
      attitudeDesired.yaw = setpoint->attitude.yaw;
    }

    if (setpoint->mode.pitch == modeVelocity) {
       attitudeDesired.pitch += setpoint->attitudeRate.pitch * ATTITUDE_UPDATE_DT;
    } else {
      attitudeDesired.pitch = setpoint->attitude.pitch;
    }

    if (setpoint->mode.roll == modeVelocity) {
       attitudeDesired.roll += setpoint->attitudeRate.roll * ATTITUDE_UPDATE_DT;
    } else {
      attitudeDesired.roll = setpoint->attitude.roll;
    }

    attitudeDesired.yaw = capAngle(attitudeDesired.yaw);
  }

  if (RATE_DO_EXECUTE(POSITION_RATE, tick)) {
    positionController(&actuatorThrust, &attitudeDesired, setpoint, state);
  }

  if (RATE_DO_EXECUTE(ATTITUDE_RATE, tick)) {
    // Switch between manual and automatic position control
    if (setpoint->mode.z == modeDisable) {
      actuatorThrust = setpoint->thrust;
    }
    if (setpoint->mode.x == modeDisable || setpoint->mode.y == modeDisable) {
      attitudeDesired.roll = setpoint->attitude.roll;
      attitudeDesired.pitch = setpoint->attitude.pitch;
    }

    attitudeControllerCorrectAttitudePID(state->attitude.roll, state->attitude.pitch, state->attitude.yaw,
                                attitudeDesired.roll, attitudeDesired.pitch, attitudeDesired.yaw,
                                &rateDesired.roll, &rateDesired.pitch, &rateDesired.yaw);

    // For roll and pitch, if velocity mode, overwrite rateDesired with the setpoint
    // value. Also reset the PID to avoid error buildup, which can lead to unstable
    // behavior if level mode is engaged later
    if (setpoint->mode.roll == modeVelocity) {
      rateDesired.roll = setpoint->attitudeRate.roll;
      attitudeControllerResetRollAttitudePID();
    }
    if (setpoint->mode.pitch == modeVelocity) {
      rateDesired.pitch = setpoint->attitudeRate.pitch;
      attitudeControllerResetPitchAttitudePID();
    }

    // TODO: Investigate possibility to subtract gyro drift.
    attitudeControllerCorrectRatePID(sensors->gyro.x, -sensors->gyro.y, sensors->gyro.z,
                             rateDesired.roll, rateDesired.pitch, rateDesired.yaw);

    attitudeControllerGetActuatorOutput(&control->roll,
                                        &control->pitch,
                                        &control->yaw);

    control->yaw = -control->yaw;

    cmd_thrust = control->thrust;
    cmd_roll = control->roll;
    cmd_pitch = control->pitch;
    cmd_yaw = control->yaw;
    r_roll = radians(sensors->gyro.x);
    r_pitch = -radians(sensors->gyro.y);
    r_yaw = radians(sensors->gyro.z);
    accelz = sensors->acc.z;

    statet.attitude.roll = state->attitude.roll;
    float a = 0.1;
    check = state->attitude.roll;
    //check = statet->attitudeQuaternion.x;
  }

  if (tiltCompensationEnabled)
  {
    control->thrust = actuatorThrust / sensfusion6GetInvThrustCompensationForTilt();
  }
  else
  {
    control->thrust = actuatorThrust;
  }

  cmd_thrust = control->thrust; // added

  if (control->thrust == 0 && !pitchWithoutThrust)
  {
    control->thrust = 0;
    control->roll = 0;
    control->pitch = 0;
    control->yaw = 0;

    cmd_thrust = control->thrust;
    cmd_roll = control->roll;
    cmd_pitch = control->pitch;
    cmd_yaw = control->yaw;

    attitudeControllerResetAllPID();
    positionControllerResetAllPID();

    // Reset the calculated YAW angle for rate control
    attitudeDesired.yaw = state->attitude.yaw;
  }
}


LOG_GROUP_START(controller)
LOG_ADD(LOG_FLOAT, cmd_thrust, &cmd_thrust)
LOG_ADD(LOG_FLOAT, cmd_roll, &cmd_roll)
LOG_ADD(LOG_FLOAT, cmd_pitch, &cmd_pitch)
LOG_ADD(LOG_FLOAT, cmd_yaw, &cmd_yaw)
LOG_ADD(LOG_FLOAT, r_roll, &r_roll)
LOG_ADD(LOG_FLOAT, r_pitch, &r_pitch)
LOG_ADD(LOG_FLOAT, r_yaw, &r_yaw)
LOG_ADD(LOG_FLOAT, accelz, &accelz)
LOG_ADD(LOG_FLOAT, actuatorThrust, &actuatorThrust)
LOG_ADD(LOG_FLOAT, roll,      &attitudeDesired.roll)
LOG_ADD(LOG_FLOAT, pitch,     &attitudeDesired.pitch)
LOG_ADD(LOG_FLOAT, yaw,       &attitudeDesired.yaw)
LOG_ADD(LOG_FLOAT, rollRate,  &rateDesired.roll)
LOG_ADD(LOG_FLOAT, pitchRate, &rateDesired.pitch)
LOG_ADD(LOG_FLOAT, yawRate,   &rateDesired.yaw)
LOG_GROUP_STOP(controller)

PARAM_GROUP_START(controller)
PARAM_ADD(PARAM_UINT8, tiltComp, &tiltCompensationEnabled)
PARAM_ADD(PARAM_UINT8, noThrustNeeded, &pitchWithoutThrust)
PARAM_GROUP_STOP(controller)

LOG_GROUP_START(ctrlpidex)
LOG_ADD(PARAM_FLOAT,q1, &statet.attitude.roll)
LOG_ADD(PARAM_FLOAT,q2, &check)//state_full[4])
LOG_ADD(PARAM_FLOAT,q3, &check)
LOG_ADD(PARAM_FLOAT,q4, &check)
LOG_GROUP_STOP(ctrlpidex)
Any help would be much appreciated! :D I have been stuck on this for a couple days now. :(



tobias
Bitcraze
Posts: 2013
Joined: Mon Jan 28, 2013 7:17 pm
Location: Sweden

Re: State estimation values for controller seem incorrect

Post by tobias » Wed Jul 01, 2020 8:15 am

Could it be that you are defining the same log group in two files. Can't remember if this creates a compile error or not...

I tried quickly to replicate it but could not. I created it a bit different though with a static float q1 which I copy to from the state_t struct.

Code: Select all

#include "stabilizer.h"
#include "stabilizer_types.h"

#include "attitude_controller.h"
#include "sensfusion6.h"
#include "position_controller.h"
#include "controller_pid.h"

#include "log.h"
#include "param.h"
#include "math3d.h"

#define ATTITUDE_UPDATE_DT    (float)(1.0f/ATTITUDE_RATE)

static bool tiltCompensationEnabled = false;

static attitude_t attitudeDesired;
static attitude_t rateDesired;
static float actuatorThrust;

static float cmd_thrust;
static float cmd_roll;
static float cmd_pitch;
static float cmd_yaw;
static float r_roll;
static float r_pitch;
static float r_yaw;
static float accelz;

static float q1;

void controllerPidInit(void)
{
  attitudeControllerInit(ATTITUDE_UPDATE_DT);
  positionControllerInit();
}

bool controllerPidTest(void)
{
  bool pass = true;

  pass &= attitudeControllerTest();

  return pass;
}

static float capAngle(float angle) {
  float result = angle;

  while (result > 180.0f) {
    result -= 360.0f;
  }

  while (result < -180.0f) {
    result += 360.0f;
  }

  return result;
}

void controllerPid(control_t *control, setpoint_t *setpoint,
                                         const sensorData_t *sensors,
                                         const state_t *state,
                                         const uint32_t tick)
{
  if (RATE_DO_EXECUTE(ATTITUDE_RATE, tick)) {
    // Rate-controled YAW is moving YAW angle setpoint
    if (setpoint->mode.yaw == modeVelocity) {
       attitudeDesired.yaw += setpoint->attitudeRate.yaw * ATTITUDE_UPDATE_DT;
    } else {
      attitudeDesired.yaw = setpoint->attitude.yaw;
    }

    attitudeDesired.yaw = capAngle(attitudeDesired.yaw);
  }

  if (RATE_DO_EXECUTE(POSITION_RATE, tick)) {
    positionController(&actuatorThrust, &attitudeDesired, setpoint, state);
  }

  if (RATE_DO_EXECUTE(ATTITUDE_RATE, tick)) {
    // Switch between manual and automatic position control
    if (setpoint->mode.z == modeDisable) {
      actuatorThrust = setpoint->thrust;
    }
    if (setpoint->mode.x == modeDisable || setpoint->mode.y == modeDisable) {
      attitudeDesired.roll = setpoint->attitude.roll;
      attitudeDesired.pitch = setpoint->attitude.pitch;
    }

    attitudeControllerCorrectAttitudePID(state->attitude.roll, state->attitude.pitch, state->attitude.yaw,
                                attitudeDesired.roll, attitudeDesired.pitch, attitudeDesired.yaw,
                                &rateDesired.roll, &rateDesired.pitch, &rateDesired.yaw);

    // For roll and pitch, if velocity mode, overwrite rateDesired with the setpoint
    // value. Also reset the PID to avoid error buildup, which can lead to unstable
    // behavior if level mode is engaged later
    if (setpoint->mode.roll == modeVelocity) {
      rateDesired.roll = setpoint->attitudeRate.roll;
      attitudeControllerResetRollAttitudePID();
    }
    if (setpoint->mode.pitch == modeVelocity) {
      rateDesired.pitch = setpoint->attitudeRate.pitch;
      attitudeControllerResetPitchAttitudePID();
    }

    // TODO: Investigate possibility to subtract gyro drift.
    attitudeControllerCorrectRatePID(sensors->gyro.x, -sensors->gyro.y, sensors->gyro.z,
                             rateDesired.roll, rateDesired.pitch, rateDesired.yaw);

    attitudeControllerGetActuatorOutput(&control->roll,
                                        &control->pitch,
                                        &control->yaw);

    control->yaw = -control->yaw;

    cmd_thrust = control->thrust;
    cmd_roll = control->roll;
    cmd_pitch = control->pitch;
    cmd_yaw = control->yaw;
    r_roll = radians(sensors->gyro.x);
    r_pitch = -radians(sensors->gyro.y);
    r_yaw = radians(sensors->gyro.z);
    accelz = sensors->acc.z;
    
    q1 = state->attitudeQuaternion.q1;
  }

  if (tiltCompensationEnabled)
  {
    control->thrust = actuatorThrust / sensfusion6GetInvThrustCompensationForTilt();
  }
  else
  {
    control->thrust = actuatorThrust;
  }

  if (control->thrust == 0)
  {
    control->thrust = 0;
    control->roll = 0;
    control->pitch = 0;
    control->yaw = 0;

    cmd_thrust = control->thrust;
    cmd_roll = control->roll;
    cmd_pitch = control->pitch;
    cmd_yaw = control->yaw;

    attitudeControllerResetAllPID();
    positionControllerResetAllPID();

    // Reset the calculated YAW angle for rate control
    attitudeDesired.yaw = state->attitude.yaw;
  }
}


LOG_GROUP_START(controller)
LOG_ADD(LOG_FLOAT, cmd_thrust, &cmd_thrust)
LOG_ADD(LOG_FLOAT, cmd_roll, &cmd_roll)
LOG_ADD(LOG_FLOAT, cmd_pitch, &cmd_pitch)
LOG_ADD(LOG_FLOAT, cmd_yaw, &cmd_yaw)
LOG_ADD(LOG_FLOAT, r_roll, &r_roll)
LOG_ADD(LOG_FLOAT, r_pitch, &r_pitch)
LOG_ADD(LOG_FLOAT, r_yaw, &r_yaw)
LOG_ADD(LOG_FLOAT, accelz, &accelz)
LOG_ADD(LOG_FLOAT, actuatorThrust, &actuatorThrust)
LOG_ADD(LOG_FLOAT, roll,      &attitudeDesired.roll)
LOG_ADD(LOG_FLOAT, pitch,     &attitudeDesired.pitch)
LOG_ADD(LOG_FLOAT, yaw,       &attitudeDesired.yaw)
LOG_ADD(LOG_FLOAT, rollRate,  &rateDesired.roll)
LOG_ADD(LOG_FLOAT, pitchRate, &rateDesired.pitch)
LOG_ADD(LOG_FLOAT, yawRate,   &rateDesired.yaw)
LOG_GROUP_STOP(controller)

LOG_GROUP_START(crtstate)
LOG_ADD(LOG_FLOAT, q1, &q1)
LOG_GROUP_STOP(crtstate)


PARAM_GROUP_START(controller)
PARAM_ADD(PARAM_UINT8, tiltComp, &tiltCompensationEnabled)
PARAM_GROUP_STOP(controller)

bma
Beginner
Posts: 2
Joined: Fri Jun 19, 2020 9:45 pm

Re: State estimation values for controller seem incorrect

Post by bma » Wed Jul 01, 2020 10:13 am

I figured out what the issue was! I had set the log group variables to type PARAM_FLOAT instead of LOG_FLOAT accidentally. (Oops :cry: )

Code: Select all

LOG_GROUP_START(crtstate)
LOG_ADD(PARAM_FLOAT,q1, &q1)
LOG_GROUP_STOP(crtstate)